I've seen several posts with questions about running power and thought I would offer what worked for me.

I ran a piece of #10 direct burial from the house to my dock (about 350 feet) to power my irrigation pump. The pump runs on 230v, so I ran 10/2 wire. I didn't need a neutral and 10/2 is considerably cheaper than 10/3.

This was a bad move because without the neutral wire, I didn't have 115v for a light, radio, or utility outlet at the dock. So I bought a 115/230 volt outdoor rated transformer for $38 on eBay. It is rated for 500 watts, enough for anything I might need at the dock, but they are available in larger sizes. Be sure to shop around, these things can be very pricey, but can be found very cheap.

This is the one I got for $38

So now I have both 115 and 230 volts available at the dock and only had to run a single piece of two conductor wire which saved me more than the cost of the transformer. I might have been able to run #12 instead of #10 since the feeder is 230v, but this is not a good place to cheap out.

Simply, the transformer input is 230 volts, the output is two hots, each 115 volts, plus a neutral.

Hope this helps somebody.


Hey Moe, I'm trying to think but nuthin's happening!
Joined: Aug 2002
Posts: 20,043
Likes: 1
Hall of Fame
Lunker
Hall of Fame
Lunker
Joined: Aug 2002
Posts: 20,043
Likes: 1
Jersey,

I don't know much about electricity but my electrician (My dad) installed a GFI on mine at the pond in case of the unforseen when it comes to water. Do you have that? If not I would suggest getting it.


If pigs could fly bacon would be harder to come by and there would be a lot of damaged trees.






Joined: Jan 2006
Posts: 2,386
B
Ambassador
Field Correspondent
Lunker
Ambassador
Field Correspondent
Lunker
B Offline
Joined: Jan 2006
Posts: 2,386
How deep is good enough if you're sure there will be no more digging in the future?


Do nature a favor, spay/neuter your pets and any weird friends or relatives.
Joined: Aug 2002
Posts: 20,043
Likes: 1
Hall of Fame
Lunker
Hall of Fame
Lunker
Joined: Aug 2002
Posts: 20,043
Likes: 1
 Originally Posted By: Bob-O
How deep is good enough if you're sure there will be no more digging in the future?


I must have scared Jersey away Bob. \:\(


If pigs could fly bacon would be harder to come by and there would be a lot of damaged trees.






Joined: Jan 2009
Posts: 10,458
Likes: 3
C
Ambassador
Field Correspondent
Hall of Fame
Lunker
Ambassador
Field Correspondent
Hall of Fame
Lunker
C Offline
Joined: Jan 2009
Posts: 10,458
Likes: 3
 Originally Posted By: Bob-O
How deep is good enough if you're sure there will be no more digging in the future?


From having dug around utilities, its insane how shallow the electric company buries their wires. Anywhere from 6" to 12" IME. So I guess it would work for the non professional.

Joined: Feb 2005
Posts: 4,025
Likes: 2
B
Lunker
Lunker
B Offline
Joined: Feb 2005
Posts: 4,025
Likes: 2
If a local deep ground rod was driven, there would have been 2 115 vac circuits with the ground as neutral to each hot line.

Last edited by burgermeister; 06/21/09 12:17 AM.

Joined: Jan 2005
Posts: 469
J
Lunker
Lunker
J Offline
Joined: Jan 2005
Posts: 469
Sorry for the late reply. I don't have internet at the house (dial up does not count).

The buried wire is about 4'. I ran it in the same ditch as the geothermal pipes.

Technically, it might work to use the ground wire for neutral, but that is a rule that I don't want to break. And you couldn't use a GFI outlet if you do this. If you put a ground rod at the end of the run (by the dock) you would have the potential for a very bad ground loop situation, because the other end of the wire is already grounded at the panel. Believe me, before I came up with the transformer idea, all of this crossed my mind. There are just too many dangerous problems associated with using ground as neutral.


Hey Moe, I'm trying to think but nuthin's happening!
Joined: Feb 2005
Posts: 4,025
Likes: 2
B
Lunker
Lunker
B Offline
Joined: Feb 2005
Posts: 4,025
Likes: 2
Jersey, I see. You actually got a 0.5 kva isolation transformer for $38 bucks. Very good deal. I fugured it was an auto former. Did you ground the case and/or neutral? Good info.


Joined: Jan 2005
Posts: 469
J
Lunker
Lunker
J Offline
Joined: Jan 2005
Posts: 469
The center tap of the secondary, which is neutral, is grounded.


Hey Moe, I'm trying to think but nuthin's happening!

Link Copied to Clipboard
Today's Birthdays
2catmom, Snoopy
Recent Posts
Feeders - I know - asked many times
by 10x - 09/20/26 06:58 AM
Stop Feeding- Will Bass Return to Foraging ?
by Pond Star - 09/19/26 11:41 PM
Gravel Pit Lake - Aeration ?
by 4CornersPuddle - 09/19/26 03:45 PM
Iron Ore Well Water
by FishinRod - 09/17/26 10:21 AM
Field and Stream Feeds?
by Bill Cody - 09/14/26 07:37 PM
Newbie from Colorado
by ewest - 09/14/26 03:34 PM
New Pond Update...
by ewest - 09/14/26 03:27 PM
Too much forage?
by Jst4Fun - 09/14/26 01:09 PM
Lotus variety of nice color
by gehajake - 09/13/26 02:07 PM
Billboard Tarp Pond
by jason7858 - 09/11/26 05:21 PM
LMB in 1 ac pond
by Terry Battisti - 09/11/26 04:10 PM
Previous lurker from Dayton, Ohio!
by ewest - 09/10/26 10:03 AM
Newly Uploaded Images
Uninvited crappie pictures
Uninvited crappie pictures
by fishwife, June 16
Chestnuts this afternoon
Chestnuts this afternoon
by Rangersedge, May 21
Trackhoe
Trackhoe
by Rangersedge, January 24
Thanksgiving RES
Thanksgiving RES
by Shorty, November 27
Nice 12 Inch BGxRES
Nice 12 Inch BGxRES
by Theo Gallus, June 1
F1 Bass stocked 6/24 caught 3/30/25
F1 Bass stocked 6/24 caught 3/30/25
by lafarmpondguy, March 31

� 2014 POND BOSS INC. all rights reserved USA and Worldwide

Powered by UBB.threads™ PHP Forum Software 8.0.1