BGK, as far as the wiring goes... what size wire did you run? the size of the breaker that you need depends on the amount of amps that you intend to use...but then also you need to run the appropriate sized wire for that amount of amperage and take into account voltage drop over long distances.
okay so normally a 15 amp circuit would call for 14 gauge wire...a 20 amp circuit would call for 12 g wire. (this is for copper wire btw, not aluminum) you said you have a 575 foot run??? im not an electrician but as the run gets longer it is a good idea to bump up the wire size a bit to help prevent a voltage drop. in you case that is a real long run so you should bump it way up.
here is 2 links to voltage drop calculators
http://www.nooutage.com/vdrop.htm http://www.elec-toolbox.com/calculators/voltdrop.htmassuming you are running copper wire in pvc conduit both suggest #4 wire...yikes that is some big wire.
if it was me id put a new 20 amp breaker in your electric panel and run 4g wire..jmo
if you run it off an existing outlet...lets say a 15 amp, if the pump and fans pull 10 amps while running then that doesnt leave you much power left in that 15 amp circuit, if you use anything else in that circuit with 5 amps or more of power you will flip the breaker.
justin